23/11/2021
We would like to cycle the quadrupoles in the linac. The procedure of the cycling was provided by Cynhia (attached).
The magnet current should be ramped from 0 to IMAX , decreased down 0 and ramped back to IMAX three more times. Measurement current will be finally reached going to nominal current ISet. (IMAX = 12 A).
Total cycling time is ~8 min [so ~1 min for 0 to IMAX, and the same for IMAX to 0). Waiting time at IMAX & I=0 is ~10 sec.
More probably this procedure is driven by the fact that the B(I) curves were provided for the positve values of I only I = 0..+12
As it was discussed with Cynthia: In order to set the negative current (defocusing quadrupole magnets), the cycling procedure should be reversed.
When the calibration curves [-12 A +12 A] will be available, the procedure has to be the following. The magnet current should be ramped from 0 to IMAX , decreased down to -IMAX and then ramped again up to IMAX.
Measurement current will be finally reached going to nominal current ISet. (IMAX = 12 A). Total cycling time is ~6 min [so ~1 min for 0 to IMAX, and the same for IMAX to - IMAX). Waiting time at IMAX & I=0 is ~10 sec.
Figure attached: Quadrupole cycling layout given by Cynthia.
Figure attached: Quadrupole cycling layout in case of bipolar power supplies and corresponding calibration curves.
For the linac, to set the quadrupoles to 0, we can use the last procedure involving the + I max and -Imax (figures attached) and for later, we should discuss with Fabrice Marteau how we procceed.
We made the cycling for the QUAD qnd still we have 5-10 G of the remaining field. To be understood....
|